| FT1 |
FT1 Vertical Flame Test — per C.S.A. C22.2 No. 0.3-92 Para 4.11.1
A finished cable shall not propagate a flame or continue to burn for more than one (1) minute after five (5) fifteen (15) second applications of the test flame. There is an interval of fifteen (15) seconds between flame applications. The flame test shall be performed in accordance with Para 4.11.1 of Canadian Standards Association (CSA) Standard C22.2 No. 0.3. In addition, if more than 25% of the indicator flag is burned, the test cable fails. FT1 Cables can be used in Combustible buildings. |
| FT4 |
FT4 Vertical Flame Test — Cables in Cable Trays per C.S.A. C22.2 No. 0.3-92 Para 4.11.4
The FT4 Vertical Flame Test — Cables in Cable Trays is similar to the UL-1685 Vertical Tray Flame Test, but is more severe. The FT4 test has its burner mounted at 20° from the horizontal with the burner ports facing up. The UL-1685 Vertical Tray has its burner at 0° from the horizontal. The FT4 samples must be larger than 13mm (.512″) in diameter. If not, then the cable samples are grouped in units of at least three (3) to obtain a grouped overall diameter of 13mm. The UL-1581 Vertical Tray does not distinguish on cable size. The FT4 has a maximum char height of 1.5 m (59″) measured from the lower edge of the burner face. The UL-1685 has a flame height allowable up to approximately 78″ measured from the burner. FT4 Cables can be used in Non-Combustible buildings. |
Combustible Construction
Combustible Construction; means that type of construction that does not meet the requirement for noncombustible construction. Combustible means that a material fails to meet the acceptance criteria of CAN/ULC S114, (Standard Method of test for determination of non-combustibility in Building Materials) (ref: NBC Part 1 Section 1.1.3.2).
Noncombustible Construction
Non-Combustible Construction; means that type of construction in which a degree of fire safety is
attained by the use of noncombustible materials for structural members and other building
assemblies. Non-Combustible means that a material meets the acceptance criteria of CAN/ULC S114, (Standard Method of test for determination of non-combustibility in Building Materials) (ref: NBC Part 1.1.3.2). |
Cable Substitution Hierarchy as per C22.2 #214 — Communication Cables
The following cable substitution may be used:
A. Communication cables marked MPP, CMP, MPR, CMR, MPG, CMG, MP, CM, CMX, CMH, FT6, and FT4 have been found to meet the standard criteria for FT1.
B. Communication cables marked MPP, CMP, MPR, CMR, MPG, CMG, and FT6 have been found to meet the standard criteria for FT4.
C. Communication cables marked MPP and CMP have been found to meet the standard criteria for FT6.